Question 56
In a run requiring 15 m (50 ft) of cable between the floor distributor and the consolidation point, the MAXIMUM length of cable allowed between the CP and the telecommunications outlet is:
27.4 m (90 ft)
36.5 m (120 ft)
45.8 m (150 ft)
75 m (242 ft)
90 m (295 ft)
Question 57
When specifying telecommunications outlet boxes, all of the following should be considered EXCEPT:
Outlet box shall be a minimum of 100 mm (4 in) x 100 mm (4 in) x 76 mm (3 in)
Outlet boxes should be installed near an electric outlet at the same height
Different outlet boxes have different support requirements
Floor mounted telecom outlet boxes should be coordinated with furniture to minimize the potential trip hazard
Outlet boxes must be of adequate size so that minimum cable bend radius requirements are not exceeded
Question 58
Which of the following is NOT an example of a perimeter pathway?
Furniture pathways
Surface raceways
Multi channel raceways
Under carpet cabling
Raceways integrated within walls
Question 59
When placing an optical fiber cable in the horizontal optical fiber cabling subsystem, what is the MAXIMUM number of splices that can be used?
1
2
3
4
5
Question 60
From a 1000 ft (305 m) roll of optical fiber, how many MAXIMUM length centralized optical fiber cabling runs can be made?